Oct 23, 2002 #1 llwydarth Electrical Joined Oct 23, 2002 Messages 1 Location GB Could anyone please advise me as to the IEEE requirements for wiring a 9.5 Kw electric shower
Oct 24, 2002 #2 wbd Electrical Joined May 17, 2001 Messages 659 Location US Off the top of my head I can't think of any IEEE requirements for a shower. Are you refering to the water heater for the shower? Whatever requirements there are would be electrical code rfequirements. Upvote 0 Downvote
Off the top of my head I can't think of any IEEE requirements for a shower. Are you refering to the water heater for the shower? Whatever requirements there are would be electrical code rfequirements.
Oct 25, 2002 1 #3 welshwizard Electrical Joined Aug 18, 2002 Messages 18 Location GB In UK circuit must have a 0.4 sec disconnection time Watch out for supplementary equipotential bonding A 30mA RCD can be fitter to reduce shock risk Read BS7671 Part 6 Section 601 for Locations containing a bath or shower Upvote 0 Downvote