ThePunisher
In NEC 250, provision of ground rods is focused mainly on the fact that they are there facilitate dissipation of static voltages and lightning induced surges. The system is provided with equipment grounding conductors (EGCs) to establish an effective path for the ground fault to return to its source. In the code, it is also emphasized that the ground (via rods or grounding electrodes) is NOT an effective ground fault current path and if current does go through it due to no EGCs, it will may not trip the OCPD and will create potential gradients.
In IEEE 80 on substation grid design on the other hand, it is assumed that a ground fault will get injected into the grounding grid (where the equipment grounding is bonded directly to the grounding grid). The ground mesh I designed in such a way that it would result to smaller "scallops" of potential gradients based on the largest ground fault current injected into the grid (not to mention that this ground fault current is further reduced into smaller grid currents).
a). However, what if the substation is Code compliant such that EGCs are installed and bonded between the transformer secondary and the main switchgear wherein an effective current path is established and the conductor is sized to carry the full ground fault current. Can we safely assume that a single loop grid encircling the building will suffice?
b) Will it be right for me to say that IEEE 80 grounding grid design is mainly focused on the deliberately designing the system so that the ground fault current is (of if) injected to the grid will not cause any intolerable touch/step voltages or potential gradients as it is based on a design that the "earth" is being used as an effective current path?