Hello All,
I see that in the IEEE 80-2000 Curves to approximate the split factor Sf we have the choice between Transmission line and feeders for the curves.
I understand that transmission line is when you have only 3 phases (HV MV),
and feeders when you have 3 phases + neutral (LV).
It seems that there is no difference between 3 phases line cables and 3 phases buried cable with shield. I am sure that there is something I havn't catch.
If I have for example a substation with 2 incoming lines in 33kV cables (so only 3 phases) and 10 11Kv outgoing feeders by buried cables (only 3 phases also but buried with shielded cables).
In The substation I have 2 Delta / Wy transformers (not in parallel each transformer supply his 5 feeders or 1 supply 10) The worst case is 1/5 I suppose.
Neutral is limit to 1000A (at the upstream substation) at the primary and limited to 300 Amps by a resistor in the current substation at the secondary.
I have a substation grid resistance of 2 Ohms
I am in 100 % Remote contribution (no generator in the substation)I think I have the choice between figures C13 C14.
Difference between C13 and C14 is the value of Transmission GND 15 ohms and 100 ohms.
As I don’t know these values I could choose the worst case,100 ohms for transmission ground. (how I can obtain these value ?)
So for my example I will have approximatively 35% of Sf.
I s it right ? I don’t see in this example how I make the difference between buried cables (with shield) and line (with only guard cable) .
Thanks by advance for your patience and your explanations.