jraef
For industrial motors IEC60034-1:1996 applies (formerly known as IEC 34-1) "Rating and performance". There is simply no IEC equivalent to service factor, I didn't even know what it meant until I started seeing references to SF on this forum. I have just flicked through my copy just to make sure.
The motor rating plate usually gives the rated values of voltage, current, speed, power factor, temperature class etc, and unless otherwise stated these are for S1 duty (continuous running). Incidentally, although the motor may be capable of running over a specified voltage range, the rated values do not imply any other capability other than at the rated voltage.
In the UK (IEC territory) it has long been accepted practice to rate industrial induction motors to class B temperature rise whilst using class F insulation, except on some larger machines. However, I have never seen it equated to a particular value of service factor as you have seen ABB refer to. But I wouldn't expect to in a European brochure as we don't use the term; I have read plenty of ABB material but I guess they only make the reference in the US.
The respective temperature rises for classes B and F for a typical induction motor are 80 and 105 deg.C, I would think it reasonable that for the same motor life, the motor with class F insulation would be capable of 15% higher output than an equivalent motor with only class B. This assumes that the winding temperature goes up with the square of increased power.
When I first came across SF I thought it was a good idea, now I am a bit dubious. Having been brought up without it, it seems like an uneccessary complication but I could still be persuaded.