Therm

Mechanical
Joined
Oct 20, 2001
Messages
7
Location
GB
I wish to add Glycol to existing chilled water circulation system to protect against freezing. The percentage of Glycol to the full system water volume is 20%

What effect will this have in terns of increased pressure drop and specific heat capacity.

Is there a percentage that can be is added to the friction losses of the standard pipe sizing data that makes allowance for any effect that the Glycol will have upon the system.

Regards,

Therm
 
I don't have the answers but the following web site ( is for Houghton Chemicals who were able to provide me with data for our densitometer (used for glycol dilution control). Incidently, if you need online glycol dilution measurement then go to
 
Do a search for Dow's glycol solutions (SR-1 I believe?). They have information on pressure drops for various glycol(s) solutions. If it's not available on line, you can request the technical information.
 
Therm,

Try this link..... you should be able to get the thermal properties info that you need


The short answer to your question is.... "not much change at 20%".... the thermal properties of Glycol (ethylene or propylene)are not that much different than water

Good luck

MJC
 