Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations JAE on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Hydrostatic Test

Status
Not open for further replies.

JATE

Mechanical
Joined
Jan 10, 2014
Messages
57
Location
PE
Good day:

When the NDT tests have been carried out at 100% of the welded joints, the hydrostatic tests must be carried out or they may not be carried out in b31.3.

We have made a line of 3 km of tailings of 34 ".

Thanks for your help


Juan Torres
 
A hydrostatic test or a leak test is mandatory as per 345.1 to ensure tightness of the piping system.
Prior to initial operation, and after completion of the
applicable examinations required by para. 341, [highlight #FCE94F]each piping
system shall be tested to ensure tightness[/highlight]
 
Juan,
If your design is B31.3 you must follow the requirements - hydrotest required.
Without more information I would question why B31.3 is being used for 3km of above ground tailings ?
Regards,
Shane
 
It may be depended on the service fluid category and what are types of NDT tests have been performed, and if this is a "golden weld" as defined and acceptable by the Client.
 