Hydraulic Design Information Sign

Status
Not open for further replies.

jjmoore73

Mechanical
Joined
Apr 13, 2011
Messages
30
Location
US
Many times we have 3 story buildings. The 3rd floor is the only one calculated, the other two floors are piped typical to the hydraulic design on the 3rd floor. The hydraulic design sign is attached to the 3rd floor control valve. Is a hydraulic sign required on the 1st and 2nd floor control valves. I ask this question with NFPA 25 in mind. ITM department is writing up missing signs. Engineering department insists the signs are not required because there was no hydraulic design for that floor.
 
Normally see in the riser room
Seems to make sense for it to be there

Have to see if 13 specifies where it should be
 
13-2010

24.5.1


Says at the alarm valve
 
cdafd, interesting that the example hydraulic placard in that coffee break training attachment is filled out incorrectly. Heckuva water supply required to provide 337.15 gpm per sq. ft over an area of 1950 sq. ft.
 
Haha. Always good for a Monday morning chuckle SK. I'd say at least 50% of the hyd. signs I see are filled out wrong.

R M Arsenault Engineering Inc.
 