If it is an existing unit then you can calculate the actual tonnage by taking DBT, WBT at inlet and outlet of the cooling coil and flowrate in cfm.
You get the load Q (btu/hr) = 4.5 x cfm x (h1-h2) where h1 is inlet enthalpy in btu/lb(corresponding to inlet DBT and WBT, from a psychrochart) and h2 is outlet enthalpy. Tonnage calculation is already covered in previous post.