i can't decipher the coincidence language... but typically you use the 1% and 99% percentile of the climate data, which will represent a design OAT for heating and cooling.
If you use 1%, 99%, 99.6% is up to what you want or the owner wants, or code prescribes. Code also may prescribe something in addition. Here in WI the ASHRAE recommendation is -11°F (based on 1% i believe), code requires -15°F... so following the percentile rule is moot since you need to meet code.