General Retrofit Procedure: Centrifugal, Reciprocating AC and Refrigeration Systems
1. If the system is able to run – collect system data and operating conditions prior to retrofit.
2. Isolate the compressor and recover the R-12. Change the lubricant in the compressor to
polyol ester (POE). For hermetic compressors this may require removal of the compressor.
3. Replace any oil in auxilliary components such as oil separators or oil feed systems.
4. Close the system and run with R-12 for 24 hours to circulate the POE and flush the mineral
oil back to the compressor.
5. Repeat steps 1-4 until residual mineral oil level is below 5%. (If the unit is not operational
then perform the oil flushing procedure immediately after startup with R-134a.)
6. Recover the R-12 from the entire system.
7. Perform any maintenance, repair or component replacements, and change filter/driers.
8. Evacuate the system to manufacturer’s specifications.
9. Charge the system with the proper amount of R-134a (usually 85% to 90% of the original
R-12 charge by weight).
10. Operate the system and record new system operation data. Make adjustments to controls
as needed to ensure proper operation.
11. Label the system with the new refrigerant and lubricant type.
Most Common Areas that Require Adjustment or Attention:
• Changing the lubricant to POE
• TXV valve adjustment / superheat setting