Thanks for your answer. CBFP I want to have is exactly the same as CBFP of REF610. To give you more information, I have taken some sentences from REF610 "Technical Reference Manual" about its CBFP: "The CBFP can also be selected to be triggered externally by applying a digital input signal to the relay. In this case, the CBFP generates a trip signal via an output if the current has not been cut off on expiration of the set operate time. External triggering is inhibited when all currents fall below 12 percent of the rated current In. External triggering is selected by activating CBFP in switchgroup SGB".
I use two relays, REL670 for main protection, REF541 for backup protection. Trip signal from REL670 is connected to a digital input of REF541 to trigger CBFP of REF541. When a fault occurs, trip signal from REL670 is sent to REF541, after a settable delay time and the current has not been cut off, REF541 will issue a CBFP signal via a digital output.
When I use CAP505 to configure REF541, I try to find a function block with the name CBFP (or 50BF...) to meet my need but there is not any. The only thing I found is the CBFP outputs from protect function blocks.