How to install tie rods to counter roof thrust in a barn with a central post obstruction?
marieVy
Agricultural
Hello everyone,
I'm looking for advice on the best structural approach for stabilizing the walls of an old timber frame barn.
● In short: How do you install a cost-effective anchor plate system where the tie-rod runs under a truss, bypassing its central support post without contact with the post and the timber frame?
The only solution I found is to run the rod just along the side of the post on the external side of each post. The rod would not be exactly under the truss but using a 80x50cm X shaped anchor plate aligned horizontally (cf the picture), at least one half of the X could maintain the wall under the truss rafters. But would it work if the center of the anchor plate isn't aligned under the truss rafters?
● In detail:
The Issue:
The trusses are a "raised tie beam" design, which exerts significant outward thrust on the 5 m (16ft) high masonry walls. This is causing the walls to spread and the corners to crack, with fissures on all four sides (on one side, it is running from the top all the way to the ground).
EDIT: , I forgot to mention that the mortise and tenon joint at the post's apex has failed. The truss rafters have visibly slipped downwards and away from the post. It appears to be held only by two bolted metal plates, but I don't know if this repair was made before or after the slippage occurred (see updated photo below). So it seems that the central post is not providing the assumed ridge support, and the frame might be subject to significant outward thrust, explaining why the cracking is confined to the corners. (cf? the picture)
The standard solution would be to install horizontal tie rods across the 9 m (30ft) span, located directly under each of the two trusses to counteract the thrust effectively.
Problem with the posts:
The effectiveness of a tie rod depends on its placement directly under the truss. However, the central post supporting each truss stands exactly in the direct path where the tie rod should run. This prevents a simple, straight-line installation from wall to wall.
My Question:
What is a cost-effective tie-rod system that can bypass the central post without contact, engaging solely with the masonry walls and placing no load on the fragile timber frame?
Aesthetics are not a concern, but cost-effectiveness and ease of implementation are important factors (e.g.: A double tie-rod system is not a feasible option due to cost and complexity)
Thank you for sharing your knowledge and practical experience.
- The barn is 9m x 14m (approx. 30ft x 46ft) with two load-bearing timber post 0.2x0.2x6.5m (8''x 8'' x 21ft) IMG_20250804_133250_5.jpgIMG_20250804_133323_5.jpgIMG_20250713_192012_5.jpgIMG_20250804_133347_5.jpgIMG_20250804_133503_5.jpg
This is the type of anchor plates I was thinking about:
Seem more likely you have settlement or seismic happening based on your photos. There really shouldn’t be thrust since the post acts similarly to a ridge beam, though the rafter could be under sized for the load. From wall should show signs of bulging. I doubt the rafter connection could transfer that much load.
What's the roof pitch? I could see some outward thrust based on the low pitch the photos appear to indicate.
Assuming all the OP's assumptions are correct, I haven't looked through the post yet, but to address the question, why are you unable to place a tie rod concentrically through the post? Posts look like they might be 8" wide or so, think you could easily drill a 5/8" hole for a half inch rod and not affect the performance of the post anymore than when someone chewed half of the upper quarter off .
Why try to attach to the masonry to resist the thrust of the rafters? Why not just attach directly to those timber rafters? I'd look at adding anchor plates to both sides of those timbers (through bolted at the ends of the timber rafters) to attach rods or cables on each side of the post.
Something similar to what you see at the ends of the steel rod in the picture above, but with one on each side of the timber rafters.
I am not seeing significant thrust here, not in the typical sense anyway, as long as there is a post at the ridge @ each frame. Ridge would need to drop for there to be much of an outward thrust component in the frames themselves.
This looks more like a simply-supported sloped beam (maybe overspanned) to me.
I just want to point out how this issue reminds me of downtown Charleston... Lots of old masonry buildings there that had issues in an earthquake back in 1886. One of the solutions was to have a metal plate on the outside of the masonry wall. This was connected to a tie rod of some sort. The Charleston issue probably wasn't exactly the same issue, of course. Probably not a truss, but more to strengthen the roof / floor anchorage to the wall to avoid pancaking of the structure.
However, I will mention it because it ended up being a pretty elegant solution for a lot of buildings in Charleston. My guess is they're still doing it for new construction. It's just so common on their buildings.
I agree with others that you shouldn't be having thrust if you have central post.
I agree about there not appearing to be thrust from sag of the peak. The rafter closest to you on the left side in picture 4 looked bowed more than others. Is it really bowed or is that just the way the picture looks?
The masonry crack the size shown in the picture for a building of this age does not look excessive to me. For any old building, it is best to take a lot of benchmark measurements including plumbness and digital photos before you start to modify it. Nice to know what is new versus old.