PYDC402040
- Apr 4, 2011
- 9
The conceptual question is - how is the horizontal component accounted for when ridge beams are used to carry the load? Yes, the rafters are designed for bending, and a large component of the gravity load is transmitted to the foundation, but there is still thrust present pushing out the walls. It looks as though rafter ties can be eliminated for engineered buildings with ridge beams, but the code also prohibits walls from resisting lateral loads.
I have a low slop building - 1.5in per foot over 25'-5" span. We'll be using microllam rafters. The architect and client do not want rafter ties, they want to see the slant of the ceiling from inside.
In my case, it seems small at each rafter - just 155 lbs of horizontal force, but the building is nearly 28 ft wide. So this multiplies out to 2175 lbs acting on each wall. Certainly needs to be accounted for.
Do you have to show moment capacity with the ridge beam posts and ends? Even if upsized to double 2x6 and reinforced the bottom connection to resist the moment of 155 lb horizontal at each rafter (over a few sections at a time), isn't this still the "wall resisting the lateral force" which isn't allowed?
I can tell the client they have to have rafter ties, but that also does not seem right as it is such a low pitch roof. Plus, I would like the architect to hire me again (LOL) and don't want to mess with her design too much! The windows will also be full height, and will be custom cut to the slope, so adding a ceiling will change the entire aesthetic, even from the outside. If you're looking at the schematics, the wall on the left has a handful of large openings and is more like a portal than a true wall (this is a sunroom that connects to the interior of a house) if that makes a difference, the largest opening the ridge beam spans is about 10'. So if I'm looking at horizontal capacity of the posts on either side of that opening it would be 387 lb at a 12 ft height.
Thank you for any guidance!