How to dump to 50% of vessel's design pressure 1
seuenergy
Chemical
HK
Hi all,
In API 521, section 4.6.6 states:" For pool fire exposure, this generally involves reducing the equipment pressure from initial conditions to a level equivalent to 50% of the vessel's design pressure within approximately 15 min."
I am wondering how we could get 50% of design pressure if the set pressure is little lower than design pressure. Thanks for your reply!
The API 521 (2020) Paragraph 4.6.6 that you reference does end with the statement "Depressurising disposal systems are discussed in 5.3.3". Maybe have a read of that.
Since you posted in the safety/relief valve forum, be also aware that Pressure-relief Valve manufacturers of old, did catalogue the availability of their spring operated pressure relief valves, fitted with a top (cap) mounted air motor that allowed the user to make the PRV to act as a dump valve. ie., open and stay open at pressures below set pressure. I'm sure they could do it now, and also with a pilot operated valve by having a solenoid fitted, that is if any of todays companies are willing to look at it properly rather than give you a AI type answer of 'it's not in the catalogue'.
The set pressure of what? A rupture disk or an ESD?
Are you confusing the PSV blowdown pressure with the pressure vessel depressuring?
More details = better answers
Hi Shvet,
Thanks for your reply.
My confusion is that if the set pressure of PSV is only little than design pressure. Like 95% of design pressure. How can we get 50% of design pressure when dumping. Thanks!
You normally dont use the PSV for this emergency "dumping". Use a dedicated depressuring valve which is forced full open through the plant's safety controls. The emergency flow through this path is constrained by a restriction orifice or by selecting a globe type valve as the depressure valve. Flow will decay as vessel pressure decays during this depressuring operation. Talk to your senior process / safety / instrumentation engineers for more details.
PSVs have nothing to do with depressurizing. You should reconsider what para. 4.6 is talking about.
Thanks Shvet, I finally got your point. That is depressurizing system not PSV.