Not to argue, but the principles Monte describes are those of a thermosyphon; as is the steam drum on a water tube boiler or the oil coolers on many industrial compressors and even rudimentary forms of heat pipes.
There are a million or more finned coil R-717 evaporators cooling air spaces from temperatures of 40-deg. down to minus 40 or so, all essentially installed with the SD operating level 6" above the topmost tube on the finned coil. Any liquid head required is in fact a penalty to heat transfer as the saturation pressure is higher and the benefits of vapor generation to convection are diluted...
Course they are all designed with 10 to 15 deg. gross TD and adjustments on the Op Liq Level....and to a level of 90% and higher effectiveness, they all work.
By contrast: the folks who put Surge Drums right on top of redwater chillers or CIP brewery chillers have risers between barrel and SD of as much as 6-feet...and liquid at 7-ft over the topmost tube. And these things are only targeting 35 to 40-deg Outlet Temps....
And earler thermosyphon oil coolers relied on some large liquid heads to drive liquid through a S & T:
The major manufactures indicate 7 to 8 feet to support a recirc rate of 3:1. Difference was: smaller refrigerant passages and a whole lot bigger temperature differences.
Only with the incorporation of plate and frames or brazed plates or drum and plates has this whole thing become a topic. Largely that because these devices were originally considered sensible heat exchangers, and their passages are nearly symetrical by nature. With 4-connections and a stack of rectangular plates, the only thing that determines the available flow area is the spacers (often single layer gaskets in a P & F) between adjacent plates...
Consider that, for R-717: The vapor volume at Minus 40 & Sat is over 20-times as great as it is at plus 40: Op Temp and Temp Difference is a big topic to those trying to fit a 50-tr HTX in a briefcase; whereas for space cooling, a similar capacity device consists of (50)-parallel 7/8" OD tubes formed into serpentines, occupying something like 350 Cu Ft. and its own vertical dimension is 6-ft or better...
Well, its just not quite comparable. And there's currently lots of R-717 brazed plates on glycol out there that make ice in a diagonal line across maybe 30% of their exposed surface; the other 70% barely even sweats.