I am a structural engineer and need to solve a problem with refused steel pipe pile.
1.This is a group of 8 (2x4) pile foundation. Concrete pedestal is located at pipe pile location. Concrete beams are provided to tie the piles together.
2. The middle pipe pile should be driven to 26m, but it hit early refusal at 13m. Geotechnical engineer abandoned the pile. Two replacement piles with smaller diameter were driven at a distance of 2.3m to the refused pile. Concrete tie beam was poured. If the capacity of refused pile was neglected, i.e. assuming the refused pile provides no vertical support, then reinforcement in the concrete beam is not enough.
3. Can we assume that the refused pile provides any support? If yes, how much(full or partial)?
Any opinion, advise and comments are welcome. Thank you very much for help.
1.This is a group of 8 (2x4) pile foundation. Concrete pedestal is located at pipe pile location. Concrete beams are provided to tie the piles together.
2. The middle pipe pile should be driven to 26m, but it hit early refusal at 13m. Geotechnical engineer abandoned the pile. Two replacement piles with smaller diameter were driven at a distance of 2.3m to the refused pile. Concrete tie beam was poured. If the capacity of refused pile was neglected, i.e. assuming the refused pile provides no vertical support, then reinforcement in the concrete beam is not enough.