We know that motor peak inrush current (first cycle) can vary randomly based on the phase angle of the voltage at the time of closiong.
Let's say I start the motor many times and each time record the single highest magintude peak (either polarity, any phase) for each start.
Assuming ideal conditions (simultaneous contact closure on all 3 phases without bounce, balanced voltage, no motor assymetries), what would you estimate the variability of these recorded numbers as as a result of random variation of voltage phase at time of closing?
From a simple R/L circuit model, I estimated around 6% variability (max peak minus min over average) at pf = 0.15. Spreadsheet attached (don't look at the cell formula's... they are uglier than they need to be). Seems like surprisingly low variability. Maybe I made an error?
What do you estimate?
=====================================