Have you taken into account that altering the fan speed will vary the CFM moved by the fan, the static pressure varies also and the brake horsepower will also vary, so given the good advice about the proper pulleys to use here goes the other formula you will need:
1.- CFM (cubic feet per minute) varies with fan speed:
Q2 is to RPM2
as Q1 is to RPM1 being Q1 initial volume displaced
Q2 final volume displaced
RPM1 initial FAN speed
RPM2 final FAN speed
2.- Static pressure varies as the square of the fan speed
(SP2/SP1) = (RPM2/RPM1)^2
= (RPM2/RPM1)x(RPM2/RPM1)
3.- Brake horsepower varies as the cube of the fan speed
(HP2/HP1) = (RPM2/RPM1)^3
= (RPM2/RPM1)x(RPM2/RPM1)x(RPM2/RPM1)
so asuming that your fan has now a 1 HP motor and that you are changing final FAN speeds from 859 rpm to 1200 RPM you will find the following results:
1.- your CFM will increse to:
(1200/859) = 1.397 times or an increase of 39.7%
2.- your static pressure will increase to:
(1200/859)^2= 1.95 times or an increase of 95%
3.- your HP demand from the fan will increase to:
(1200/859)^3= 2.726 times
or you will have to install a motor that is 2.7 + times the power of the original motor, the motor speed is not relevant for this matter (it can be 1700 or 3450 rpm) just the power NEED from the fan to work at the new speed of 1200 rpm.
Take this into consideration, thats the reason diferent fan sizes are built, so that getting more air moved is achieved with less HP with a bigger fan than with a higher fan speed.
Cheers
SACEM1