I don't particularly like using influence lines for this problem because the answer seems easier to obtain by direct analysis.
The triangle on the left span is the influence line for shear just to the right of Point B resulting from a unit load placed anywhere between points A and B. If the unit load is placed at A or B, it contributes nothing to moment in span A-B or shear at B.
If the unit load, say 1k is placed at the hinge, it produces a moment of 1*12 = 12'k at point B. This in turn produces equal and opposite reactions of 12/60 = 0.2 kips at B and C, upward at B and downward at C. The influence line is linear between the hinge and either A or B.
To find the effect of a uniform load between points A and B, you need to take the area under the influence line and multiply it by w, the uniform load.
BA