XR250

Structural
Jan 30, 2013
5,990
I want to use some Hilti Kwik-Cons for a tension load in a 4" total thickness composite interior slab ( 1 1/2" deck). Hilti's catalog gives ASD pull-out values for 1 3/4" embedment but does not specify a minimum concrete thickness. I also find that their is no ESR report for this product. Just want to make sure I can use these fasteners and not have someone question it later.

Thanks
 
Replies continue below

Recommended for you

The thickness of the concrete doesn't matter - as long as it's thicker than the embedment depth of the screw - I know, I'm being a wise guy [lol].

A screw in concrete is somewhere between an undercut anchor and an adhesive anchor. There's a shallow cone failure then a shear failure. Hilit's web site indicates there is a testing report for Miami/Dade County.
 
Yup, it says it has Miami/Dade Testing and approvals but no link to a report.
 
Found a testing report for Miami. The values are less than Hilti's published values. I guess my question still remains - is it ok to use these?
 
I couldn't find the report either. You have three choices:

1. Contact Hilti for guidance
2. Use the Miami/Dade values
3. Use a different product
 
Thanks. All these new anchoring rules make me scared to go in any structure built a decade ago. :>
 
I understand your point. Sometime when I see old buildings in NYC with fire escapes I wonder what's holding them up. The NYC building code from the 19th C and most of the 20th C simply says provide a safe connection or something to that effect.
 