High x/r ratio on transmission network

Chunky12345

Electrical
Joined
Nov 2, 2023
Messages
1
Location
GB
Good morning all,

I've conducted a fault level study on PSSe on a 400kV and 275kV network and though the fault levels are within the ratings of relevant switchgear, the 3ph RMS x/r ratio is above 14 (close to 25). The initial peak current isn't over the make rating of the circuit breaker so no issues there. Am I right in thinking the only issue with a high x/r ratio is that the peak current might be higher than the make rating of the circuit breaker? Is there anything else I should be worried about?
 
Circuit breakers also need to be selected appropriate to the higher X/R, as the standard circuit breakers are designed for X/R of 14 only.
Good morning all,

I've conducted a fault level study on PSSe on a 400kV and 275kV network and though the fault levels are within the ratings of relevant switchgear, the 3ph RMS x/r ratio is above 14 (close to 25). The initial peak current isn't over the make rating of the circuit breaker so no issues there. Am I right in thinking the only issue with a high x/r ratio is that the peak current might be higher than the make rating of the circuit breaker? Is there anything else I should be worried about?
 
Depending on the type of breaker and the test standard used by the manufacturer, the interrupting rating may need to be checked (or derated) as well depending on your actual X/R vs the test value. IEC and ANSI standards and calculation methods are a little different.
 