powering2002
Dear All,
I work At Steam Power Plant 2 x 100 MW. It has Two Generator Step Up Transformer , Two Auxiliary Transformer and One Starting Transformer. The Starting Transformer is used mainly to supply auxiliary power to Main Unit during Shutdown, desalination plant, chlorination plant, Water Treatment Plant, and Office Building. It was rated 13 MVA. This starting transformer is never OFF. It operate continuously because when both main unit is Online,the starting transformer is still supply power to the desalination plant, chlorination plant, Water Treatment Plant, and Office Building. This power plant is built in 1980. So the starting transformer is about 34 years old now.
We performed Predictive maintenance including DGA analysis for all of our transformer. Based on our DGA results for Starting Transformer in the last 6 months, it is found that the Ethane (C2H6) concentration is very high. It exceed 200 ppm. Since January 2014, we have conducted 4 DGA Test. And from that tests, the C2H6 concentration is 247, 241, 253, and 256 ppm. . But this C2H6 concentration increasing trend is not followed by the increasing of the other Dissolved Gas Concentration (Co2, CH4, etc).
Here is our Latest DGA Result (21st of July 2014) for our Starting Transformer :
H2 : 60 ppm
Water : 22 ppm
CO2: 1581 ppm
CO : 108 ppm
CH4 : 97 ppm
C2H2 : 0.5 ppm
C2H4 : 9 ppm
C2H6 : 256 ppm
TDCG : 531 ppm
Oil Visual Inspection Color : BROWN
Using Roger Ratio to analyze that gas composition, it was concluded that It is NORMAL
But, we are worried about the high concentration of C2H6
My questions are:
1. Based on our latest DGA test, is Our Starting Transformer NORMAL or ABNORMAL?
2. If it is ABNORMAL, could you help us give the cause of high Concentration of Ethane Concentration?
3. Could you give use solutions or recommendation to overcome the high ethane concentration.
Thanks for your attention
H2 : 60 ppm
Water : 22 ppm
CO2: 1581 ppm
CO : 108 ppm
CH4 : 97 ppm
C2H2 : 0.5 ppm
C2H4 : 9 ppm
C2H6 : 256 ppm
TDCG : 531 ppm
My questions are: