I have been able to find 25kv 380v/220v transformerTake the rated KVA times 1000.
Divide by the rated secondary voltage to get the rated secondary current.
The rated secondary current must be equal to or greater tha the losd current.
Example:
Transformer Ratings.
10 KVA, 480/120 Volts
10,000 VA / 120 Volts = 83.3 Amps.
The 120 Volt windinhs on a 10 KVA transformer will safely support an 83.3 Amp load.
Use Amps for the load, not KVA nor kW.
Example #2
37 kW at 480 Volts and 0.8
PF = 96 Amps.
96 Amps will flow on the secondary windins of the boost transformers.
96 Amps times 120 Volts = 11520 VA or 11.5 KVA.
In this example you would need aa transformer of 11.52 KVA or greater .
Possibly 125 KVA or 15 KVA.
Warning. This is an example.
Use your own values and do your own calculation s.
D/Y 440/220v . I will open the interconnections and make the adjstment for open delta connectionDoubtful.
Wye or Delta?
The machine can work at 50/60hz base on its name plateNowhere has frequency been mentioned.
A 470-575Volt machine intended for 60 Hz may not survive 480 Volts at 50 Hz.