You have to check the generator nameplate to see if 480 Volts is an available voltage.What if user the standby 380v generator and then increase its excitation,will that affect winding withstanding?
Pit falls:Your best option is a pair of 380:110 (or the closest available ratings) transformers configured as an open delta auto-transformer.
Hello! According to the Pro Heat 35 electrical diagram you posted (see 460–575 V or CE unit 400–460 V power supply instructions), direct driving at 380 V power supply will be lower than the rated voltage range of the machine, which may easily lead to:Hi every one
A heat treatment machine (pro heat 35) works with power supply 470v/575v..please see attachment
What options I have to make this machine works on 380v power supply
You may find it educational to read other posts before posting.Hello! According to the Pro Heat 35 electrical diagram you posted
By far the cheapest, both cost of material and labour, is the open delta auto-transformer boost.Note: When selecting, you need to select sufficient capacity according to the maximum power (kW) of the machine (usually leave 10% margin); and ensure that the three-phase balance of the transformer
Thank you indeed for you engagement.Hello! According to the Pro Heat 35 electrical diagram you posted (see 460–575 V or CE unit 400–460 V power supply instructions), direct driving at 380 V power supply will be lower than the rated voltage range of the machine, which may easily lead to:
Insufficient motor torque and unstable operation
Control board/contactor life reduction or even malfunction
Insufficient heating element power and difficult to meet the heat treatment temperature standard
To use it safely and reliably at 380 V, there are several feasible solutions:
1. External step-up transformer (Autotransformer/three-phase isolation transformer)
Principle: Boost 380 V to the 400–460 V range required by the machine
Advantages: Simple solution, one-time investment, almost no change to the internal wiring of the machine
2. Use a three-phase variable frequency drive (VFD) with a step-up function
Principle: First, 380 V is rectified into DC, and then inverted to output AC above 460 V
Advantages: It can achieve speed regulation/soft start at the same time and reduce impact; the output voltage can be adjusted online to adapt to more working conditions
Note: Make sure that the selected VFD supports the "voltage boost (Boost)" or "variable frequency boost" function, and configure the output parameters
3. Static frequency converter
Principle: Similar to VFD, but more focused on voltage boost/reduction and stable output, the cost is between transformer and VFD
Advantages: small size, high efficiency; small impact on the power grid
Note: When purchasing, make sure that the continuous power and peak power can meet the startup and operation requirements of Pro Heat 35
I just wanted to confirm that with autotransformers, I don't need to meet the full kVA of the equipment, on the rated amps times the difference in voltage.Rental companies supplying the oil industry in Western Canada have both open delta and full wye autotransformers available for rent.
Many petro-chemical plants have 600 Volt systems. Almost all rental generators are 480 Volts.
When a 600 Volt plant needs temporary power, they rent a 480 volt to 600 Volt auto-transformer along with the 480 Volt generator.