Cam0
Mechanical
- Apr 22, 2019
- 2
I am an HVAC engineer trying to determine the proper amount of OA(outside air) ventilation required for a new addition of a chemical mixing factory. The room will have three 33,000gal tanks of glycerin that will be kept at 150F. The tanks will be heated by a hot oil system that pumps syntherm A-32 heat transfer fluid through 2in diam sched 40 pipe coil through the bottom of the tanks. I have the following info:
density of glycerin = 78.6 lb/ft^3
heat capacity of glycerin = .576 btu/lb-F
glycerin starting temp = 90F
glycerin ending temp = 150F
density of A-32= 47.09 lb/ft^3
heat capacity of A-32= .474 btu/lb-F
A-32 temp (constant) = 150F
flow rate of A-32 = 50gpm (529.2 lb/min)
volume of A-32(in one tank) = 3.5ft^3
total length of pipe in the tank = 160.5ft
I am trying to calculate the amount of time it takes for the A-32 hot oil coil to heat the glycerin from room temp (approx 90F) to 150F. I came up with roughly 36 million BTU in 5.3 hours, which is quite a lot. I was hoping to get some help/double check on my work.
Thank you.
density of glycerin = 78.6 lb/ft^3
heat capacity of glycerin = .576 btu/lb-F
glycerin starting temp = 90F
glycerin ending temp = 150F
density of A-32= 47.09 lb/ft^3
heat capacity of A-32= .474 btu/lb-F
A-32 temp (constant) = 150F
flow rate of A-32 = 50gpm (529.2 lb/min)
volume of A-32(in one tank) = 3.5ft^3
total length of pipe in the tank = 160.5ft
I am trying to calculate the amount of time it takes for the A-32 hot oil coil to heat the glycerin from room temp (approx 90F) to 150F. I came up with roughly 36 million BTU in 5.3 hours, which is quite a lot. I was hoping to get some help/double check on my work.
Thank you.