Looks quite helpful thanks KootK. Into this subject because once did a mass pour on a raft slab, 17,300 sq.ft x 3 feet thick, 1 pour, 1 day. Had a materials testing company install 5 sets of thermo-couples and the temp peaked at 52 degrees C 4.5 days after pour. Covered the slab with insulated tarps in the middle of July. That turned a few heads. So familiar with the problems associated.
Current problem is a chunk of concrete about 2.5' wide at the top and about six feet wide at the bottom. Vertical front face 7' high, sloped back face. the total length is 1300 feet with expansion joints every 70 feet. It ended up developing shrinkage cracks about every 6 foot o.c. about 2 days after the pour. I'm doing a structural condition assessment/forensic investigation.
This is definitely a thermal expansion problem during curing, compounded by the fact that the previously mentioned piece was poured on top of a previously poured foundation, so restrained at the base. The codes and literature tell you that you will get cracking if the outside temp differs from the inside temp by 20 degrees C, European is 19 deg C.
I'll take a look at what you sent and see if can figure out how to predict the core temp given the myriad of other variable. Thanks again.