I recently did an analysis like this for my data center. Some things to be aware of:
1. If the 210,000 Watts are the total UPS load, don't forget to take out the losses incurred by the UPS (which can be 10-20%). Unless, of course the UPS systems are in the same space as the servers.
2. Not all of the power consumed by the servers is converted to heat. This is especially true for automated tape storage robots, big onboard cooling fans, and standalone air conditioning units which are converting electricity into mechanical work instead of heat.
My method for calculating temperature rise goes like this:
210,000 Watts = 12,000 Btu/min
Assuming we start at 70F and 50% RH, The mass of 41,600 ft3 of dry air is (check psychrometric chart):
41,600 ft3 / (13.5 ft3/lb) = 3081 lb
So every minute we are adding 12,000 Btu/3081 lb,
or 3.9 Btu/lb
Again referring to the psychrometric chart, at the starting point of 70F/50RH the heat content is about 25 Btu/lb. Add 3.9 Btu/lb (moving horizontally because we assume no humdification), we end up at 28.9 Btu/lb, where the dry bulb temperature is around 85F and RH=30%.
15 degrees per minute is pretty severe, but it also seems that an 8ft ceiling is kind of low for a 40W/ft2 data center.
Imok2 is vindicated in my opinion!