Have I been wrong all these years filling out hydraulic calculation placards? 2
SprinklerDesigner2
1,264
From 1975 I have always filled out hydraulic calculation placards in the following manner.
A plain Jane OH2 grocery store having a 22' ceiling and not having interior hose racks.
I identify the location of the hydraulic calculation area. I know I am right here as I am right to identify 12 sprinklers as in the design area, it surprises me that I find a good number of placards displaying the total number (487) sprinklers on the system, and I know I am correct here as well as I am with the 1,500 sq ft discharge area.
The question comes up with the GPM discharge which I have here as 321.6 gpm which obviously does not include hose streams. My hose stream is 250 gpm but the hose stream is added at the source and NOT the base of riser. True, the GPM discharge doesn't ask for the discharge at the base of the riser but the residual pressure is asked for at the base of the riser.
If I need 55.3 psi at the base of the riser I would need more pressure at the source assuming the elevation of the base of riser and source are the same elevation. It doesn't make sense to me to put 571.6 gpm discharge at the street while using 55.3 psi at the base of the riser when the actual pressure required at the street could easily be 62.3 psi if a long run of pipe or if there's a backflow involved.
And the sign is asking for "discharge" which I interpret as discharge from inside sprinklers and hose streams IF these hose streams are taken downstream of the base of the riser.
And the "base of riser", where exactly is it? I have always taken it to mean the transition point between the underground pipe and above ground... if we have an 8" DI flange and spigot having a C-value of 140 running into steel pipe having a C-value of 120 then I have always associated my base of riser with this transition point.
Also, while I am rolling along, years ago I ran across an article, can't remember where, that called for gpm's and pressures to be rounded out to the nearest whole numbers. That my placard should read 322 gpm @ 55 psi. Makes sense to me because I find it laughable when I see a placard proclaiming 433.765 gpm @ 67.826 psi. I think Stookey will back me up on this that we're lucky to hit the real number within 5 psi and 10 gpm so what is the point of carrying numbers out to where they look ridiculous?
Also, if their his interior hose stations fed from the sprinkler then I do add the gpm allowance to the overhead at the point of connection for up to two hose racks.
I think part of the confusion comes from 50 years ago when most systems were pipe schedule and we did include hose streams at the base of the riser. Why? I don't know other than that was what the standard called for us to do.
I seem to remember as well we added hose streams at the base of the riser, even if no hose racks or downstream hydrants, for calculated systems from the 1974 standard. Is this "confusion" just a carry over?
So am I right on the placards?
If I am wrong how do you do it?
Oh, and speaking of hose racks. I haven't seen a hose station for occupant use in Georgia for 15 years. The state fire marshal ordered them all removed so people would leave the building and not play untrained fireman. If a company insists on hose stations they may have them but all employees, 100% of all employees event he part timers, are required to attend a several day class at the state fire marshals academy to be trained on how to use fire hoses.
I include the hose streams on the placard. I've wondered if it doesn't cause confusion to someone who may be checking the backflow preventer with a flow/pressure test.
Seems it may come down to semantics. The "SYSTEM DEMAND" would be, by NFPA 13, the network of overhead pipes connecting fire sprinklers to a water main with a control valve and flow switch - of this alone one might choose to leave the hose stream off.
The example in NFPA 13 shows two lines; one for hose streams and a total flow demand. All the available placards I've seen are the same as shown attached in your post.
In short; I don't really know the 'correct' answer!
Travis,
I agree putting down the decimals is a silly thing to do but the minute I don't someone will want to see it because everyone else shows it.
And then there are placards for ESFR systems.
SD2:
Everything you've shown is correct. Now that you have presented an elegant analysis of proper preparation of the Hydraulic Design Information Sign, can we start working towards the General Information Sign in Section 25.6 of NFPA 13? I have inspectors still asking me what's this, it's kinda cool. The same with designers who say, that's not in the book, that one of those dumb (INSERT NAME OF TOWN HERE) rules.
Discuss among yourself. I need to finish an e-mail to an architect explaining that you cannot eliminate draft stops with a NFPA 13R sprinkler system using the 2012 IBC.
Rant// Down here in the south, where it is hot and humid, those metal placards that we so carefully fill out using a magic marker are useless in ten years. They fade and the "ink or whatever" actually seems to puddle up into little dots.//Rant
So what I have taken up to doing, in addition to my metal placard, is something similar to what I show below:
I go to an office supply store and purchase a cheap wood frame for an 8 1/2" x 11" paper, drill a whole at the upper and lower corners and mount it right on the riser using plastic wire ties.
Yeah, it's wood, it's glass and paper but my general information sign will be there long after the metal hydraulic placard is unreadable and useless.
Now a secret behind the paper... I also include original signed test certificates so if someone really needs a copy in 30 years they are most likely still on site... if I did the job look behind the glass.
Below is an extract from NFPA 13, 2013 under "Hydraulic Design Information Sign"
Also note that (3) requires the flow and residual pressure at the BOR in addition to the hose stream+system demand in (5), which means the HYDRAULIC PLACARD MANUFACTURER'S MAKE THE SIGNS INCORRECTLY
not that we fill them out wrong, there aren't enough boxes on many of them.. or correct boxes..
Stookey:
I hope this is a simple question. Can you do a modified 13R in that application, design the residential portion per NFPA 13R and then provide sprinklers in the attic designed to NFPA 13 criteria? I don't know if that is permissible or not, but just wondered.
Travis Mack
MFP Design, LLC
"Follow" us at
Wow what a concept you actually hang data plates AND fill them out!! Worked in NJ for 36 years I was having a good day when they are in place. Regardless of it being required by NFPA AND NJ code they are far and few. When I taught code officials I would say if you anything make sure the contractor hangs the plate.
Guys,
When you have a fire pump do you provide the PSI and GPM for the system demand on the discharge side of the pump?
If so thanks, it makes this from NFPA 25 easy to do.
8.3.5.7 The pump performance shall be evaluated using the unadjusted flow rates and pressures to ensure the pump can supply the system demand as supplied by the owner.
So how many owners have the data or hydraulic calculations to figure this out. I wish the NFPA 13 would change the placard when pumps are involved to make this easier. Yea I know when pigs fly....
With pumps I've always recorded the gpm and psi at the pump output flange in lieu of the BOR on the hydraulic placard.
LCREP, I think providing the required total discharge and pressure requirement wouldn't be a bad thing to do on the General Information Sheet.
Below is a recently completed job, actually not 100% complete with I posted the general information sign but it was close, and you can see it's a cheap wooden picture frame with holes and wire ties.
It's glass and not plastic so I suppose I should get plastic but I do run the paper through a lamination machine so even if it does get wet the paper, hopefully anyway, won't smear.
It's on company letterhead so phone numbers and contact information is available. I also have the design standard; this particular one was for wood working and was designed per NFPA #13 2013 Edition for an Extra Hazard Group I Occupancy with a density of .24 over 3,000 sq ft with 500 gpm hose.
The building has four systems and taking a Google snapshot the red dots indicate risers (they are individually numbered), green dots indicate the location of the inspectors test connections while blue dots indicate the approximate locations of all the aux. drains.
This project had a dry pipe system and it was located and labeled as well.
Also on there is date of flow test, the location of test hydrants, results of the test and the names of those conducting the flow test. Also included is the date and results of first main drain test.
As mentioned buried in the frame is copies of five test certificates (underground and four systems) so in 10 years if an insurance inspector wants to see a copy I can tell him where to look if I am still around.
Another thing I have been doing for about five years now and that's taking video of all underground flushing operations. If someone wonders if we flushed the underground lead in to the Grand Island Hotel I can show em the video!
Travis Mack said:
Stookey:
No. You can do a NFPA 13 residential design (4 sprinkler calculation) and exclude the sprinklers from all the permissible locations but the balance of the system is required to comply with NFPA 13 (the attic). Remember, the NFPA 13 system was required most likely because the architect wanted an IBC area increase. This also means that combustible concealed spaces must be addressed.
Below is a recently completed job, actually not 100% complete with I posted the general information sign.
This will earn you a gold star. I'm having problem getting the contractor to proper post the hydraulic information and control valve signs as per NFPA para 8.16.1.1.8.