First, I would like to thank all the people who are contributing to this
Forum. Your observations are valuable to all of us who are trying to
understand this failure.
In reply to Ideem, I agree. The problem is clearly more than a bad cantilever
detail. The steel frame would should have absorbed a couple of cantilevers collapsing
without the building coming down like it did.
As to some reasons why, all of which have been quoted by others previously:
1. Bolts were shown missing in one post.
2. A weakness was identified where hardly any steel beams cross the building
longitudinally just below line 10.
3. The failure photo below show a large section of the building falling virtually intact.
4. Steel was seen in previous post not crossing steel beams at the studs, but stopping at them.
Were many bolts missing in addition to the clear design errors on the permit plans? The practice is
normally to place a couple of bolts in the beam as it is set, and before the floors are added, to place the rest.
Though the failure may or may not be related to the cantilevers, it is clear that many much more serious problems
existed at lower levels as illustrated by the photo below.
By the way, these beams are not composite steel beams. I checked a few and found that the studs were not
sufficient for composite action. They merely attach the slabs through the deck to the beams.
Regards,
Sorry. I do not know how to upload my image. Look at the failure video for part of the building falling virtually undamaged.