That is new HAP version and I assume air system put as VRF tells HAP to allocate all ventilation load to terminal units, which is plainly visible from your data (all ventilation load equals sum of terminals load).
You should alter air system type to CAV, VAV or whatever you have if you use central ventilation unit.
If those system are distinct ones, the safest way is to define your terminals as terminal units type, and use additional system as ventilation system, determined as it is in reality. Than you will have completely separated loads in the report.