Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations JStephen on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Hair Salon Load Calculation

Status
Not open for further replies.

MechGuy22

Mechanical
Joined
Jun 8, 2010
Messages
51
Location
US
Does anyone have a suggestion for a salon on what I could use for latent load per station while the hair dryer is running? Im using 1159 BTU/H for sensible heat gain. Thanks Guys
 
Depends on if they are using SOUL GLOW or not. I hear that stuff is pretty latent.
 
I figured each hair dryer is about 1700W, and they will run for about 12 minutes per hour each. 12mins/60min =.2 so 1700W x .2 hours = 340 watts x # of stations = my sensible heat load for the hair dryers. I didnt think it was reasonable to figure that all the hair dryers were running continuously all day at each station. I do think it is reasonable to figure that within one hour, each station could run their hair dryer for 12 mins. Opinion?
 
Your guess for sensible load sounds good to me. I might figure evaporating a couple ounces of water during that 12-minute time period too, or maybe four? I haven't see any recommended values anywhere.

I'd specify some de-stink-i-fyers as well, to cover myself.




Good on ya,

Goober Dave

Haven't see the forum policies? Do so now: Forum Policies
 
Your estimate sounds in line with the WAG I use - 3w/sf lights & 3w/sf misc. heat.

DRWeig (Electrical)
9 Dec 11 17:05
Your guess for sensible load sounds good to me. I might figure evaporating a couple ounces of water during that 12-minute time period too, or maybe four? I haven't see any recommended values anywhere.

I'd specify some de-stink-i-fyers as well, to cover myself.

Good one!!! I follow the same practice! I specify an ion generator (Bio-Climatic is one) on the discharge side of the air handler. Even had a client request the same be installed on the exhaust system serving the space to eliminate odors from a sidewall louver discharging to the exteriore.

Andy W.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top