I am doing a culvert span 3.5 meters, I have to limit the top slab thickness to 280mm ( no haunch possible ), it is 600 mm bury depth, H20 traffic load.
the wheel transvers spacing is 1800mm per ASShto,
since the span is 3.5m, that means I have to put 32Kipsx1.3(dynamic factor)x1.5(live load factor)=62.4 kips load on to the roof slab. this will creat fairly large moment and shear onto the slab, is this over designed?

thanks
 
The 32 kips is an axle load, not a wheel load. The two wheels are spaced a little over 1800mm transverse. I believe there is also a "design tandem" that you should analyze too. This is four smaller wheel loads instead of two larger ones.
 
The load factors are acceptable. I am a Canadian engineer but I imagine ASSHTO code would be similar and has provisions for proper load distribution.
 
Try to get a copy of the Concrete Pipe Design Manual. It has load tables #49 thru 55 set up for pipe which would be similar to your case.
 