sdz said:
I am inclined to think if we could find a flowable epoxy that we could batch in small quantities, less than 1 litre, then that would be a good solution. Did I also mention many are on rooftops in full sun so the grout has to be stable at temperatures of say 60 deg C? That could also be a problem for a lot of epoxies.
A few things to consider with epoxy resins:
1. Need to make sure the forms to the base plate are sealed well with sealant or other. The viscosity of flowable resin is such that it with otherwise leak from your forms.
2. Epoxy exposed to sunlight (UV) will discolor and go chalky over time. But, usually the exposed portion of base plate grouting is very small.
3. Glass transition temp of epoxy is typically greater than 160F (72C). You can get resins with higher heat-deflection temps that may be more applicable in you case.
4. With epoxy resins on some thickness you need to consider the exothermic reaction and reduced pot life. For thick grouting operations we usually pre-place 8mm (3/8") oven-dried basalt aggregate then flood grout the baseplate after forms are sealed etc. The use of aggregate reduces the epoxy resin volume by approx 50% ($ saved) and also the exothermic effects. The aggregate acts as a heat sink.
5. Consider plastic lining the inside face of your forms. Otherwise you will have a form well adhered to the cured epoxy.
I personally would use a cementitious based dry-pack grout in your application. You may need to make the gap between the top of concrete and underside of plate is say 25mm so you can effectively dry pack it with a hammer and wood rod etc.
Where are you located? Lots of sun and high temp, I guess.
Good luck.