Grout sequence?

Status
Not open for further replies.

ckirkland

Industrial
Joined
Jun 25, 2016
Messages
2
Location
US
Hey guys, first time poster. Question is per AISC, must erector fully tension (snap) all TC bolts prior to grouting the columns? Owner spec is undefined on the subject.

more info
A325 bolts
single story
not slip critical
 
You're not talking about the anchor rods at the column base plates, correct? You are referring to all the framing connections up above?


Check out Eng-Tips Forum's Policies here:
faq731-376
 
Correct the framing. Thanks for the information. Having a dispute with a 3rd party that insist must be completely tensioned (snapped)prior to grout.
 