I realize that the delta is not connected.
The delta does not have to be connected to anything to backfeed into a primary, grounded wye.
With fused cutout protected distribution circuits, a wye/delta bank will cause a number of serious issues on the whole circuit if a primary phase is lost.
I am wondering how primary phase loss is handled on transmission circuits feeding wye/delta/wye transformers.
Based on 15 years experience with wye/delta, I can see a wye/delta/wye transformer feeding all three phases of the secondary when a primary phase is lost. It does this by way of a circulating current in the delta.
The configuration will supply light loads.
As the secondary load increases, the delta will become overloaded and overheat.
The wye/delta/wye will also back feed into a grounded primary phase.
In the instance of a grounded primary phase, the delta may be damaged by the fault level circulating current.
Similarly a ground fault on the secondary of a wye/delta/wye transformer may damage the delta.
I am aware of all the negative effects of the wye/delta on a distribution circuit.
Most people have never had the misfortune to have experienced the negative effects of a wye/delta transformer bank on a distribution circuit.
Wye/delta circuits were common in the 40s 50s and into the 60s as old delta/delta distribution circuits were upgraded to wye/delta circuits to increase circuit capacity.
It was soon discovered to be a bad idea and the configuration has not been used for years.
I found myself in a technical time warp, where the circuit still was being installed.
The wye/delta configuration was famous for killing refrigerators and household freezers.
One wye/delta bank on an otherwise residential circuit would imperil all of the refrigerators on the same primary circuit.
My question is what protection and what settings are used on transmission circuits feeding a wye/delta/wye transformer.
Is the damage curve of the delta winding considered when designing protection schemes for wye/delta/wye transformers?
Ohm's law
Not just a good idea;
It's the LAW!