Hi,
We've found a relatively new cable installation where 2 underground feeders have been installed to service an industrial park. The cable is 750MCM Cu, 28kV concentric neutral, 3 conductors per circuit. The system voltage is 27.6kV. A separate 350 MCM Cu neutral has been installed and grounded at all switching locations.
The problem is, the concentric neutral has been connected to 3kV arresters at all locations, including the underground dip poles supplying the park. My thought is that each piece of cable should have one end of the CN solidly grounded and the other tied to an arrester to allow for the best ampacity and limit the induced shield voltage during a fault.
Any thoughts?? And thank you in advance....
We've found a relatively new cable installation where 2 underground feeders have been installed to service an industrial park. The cable is 750MCM Cu, 28kV concentric neutral, 3 conductors per circuit. The system voltage is 27.6kV. A separate 350 MCM Cu neutral has been installed and grounded at all switching locations.
The problem is, the concentric neutral has been connected to 3kV arresters at all locations, including the underground dip poles supplying the park. My thought is that each piece of cable should have one end of the CN solidly grounded and the other tied to an arrester to allow for the best ampacity and limit the induced shield voltage during a fault.