drknexus02
Electrical
- Jun 7, 2010
- 13
well i am having some confusion as far as what the NEC requires for grounding your neutral on power distribution systems...
250.2 A (5) EFFECTIVE GROUND-FAULT CURRENT PATH-
Electrical equipment and wiring and other electrically conductive material likely to become energized shall be installed in a manner that creates a low-impedance circuit facilitating the operation of the over-current device or ground detector for high-impedance grounded systems. It shall be capable of safely carrying the maximum ground-fault current likely to be imposed on it from any point on the wiring system where a ground fault may occur to the electrical supply source. THE EARTH SHALL NOT BE CONSIDERED AS AN EFFECTIVE GROUND FAULT-PATH.
now the way i understand that is that Neutral should not be connected to ground because the only reason you do that is for ground fault-paths for overcurrent conditions or for disharmony within a transformer or genset. but there are also regs like 250.184B and C. can someone clarify this for me?
250.2 A (5) EFFECTIVE GROUND-FAULT CURRENT PATH-
Electrical equipment and wiring and other electrically conductive material likely to become energized shall be installed in a manner that creates a low-impedance circuit facilitating the operation of the over-current device or ground detector for high-impedance grounded systems. It shall be capable of safely carrying the maximum ground-fault current likely to be imposed on it from any point on the wiring system where a ground fault may occur to the electrical supply source. THE EARTH SHALL NOT BE CONSIDERED AS AN EFFECTIVE GROUND FAULT-PATH.
now the way i understand that is that Neutral should not be connected to ground because the only reason you do that is for ground fault-paths for overcurrent conditions or for disharmony within a transformer or genset. but there are also regs like 250.184B and C. can someone clarify this for me?