lkincer,
From your system studies if you find Z1> Z0, then the double line to ground fault will give the maximum ground fault current. A tansformer with solidly grounded WYE on the HV side (DELTA on low side) is
a typical example which gives a higher line to line to ground fault current on the high side than single line to ground fault.