I am a newbie, so I will try not to make too much of a fool out of myself, but I need some help.
First of all, the problem: I don’t know how to properly ground a Generator -> Step Up Transformer -> Step Down Transformer.
We have a 27kva generator wired for three phase 216v Y with the center neutral earth grounded. This powers various motors and battery chargers at 216v and 125v, we are not using any three phase equipment at this time.
We also have a run of wires about ½ mile that powers another building, but we are getting too much line lose on this run. This is why I am trying to install the step up / step down Transformers.
The step up transformer is a 75kva 216v (depending on the taps) Y <-> 480v Delta transformer and the step down transformer is a 100kva 216v (depending on the taps) Y <-> 480v Delta. The step up transformer’s Y side is wired to the generator, and the Delta is wired to the Delta side of the step down transformer. I need to use the output of the step down transformer to power unbalanced 125v and 216v loads so I will need a neutral line.
I would think that the proper grounding would be to wire the center/neutral of both of the Y sides of the transformers to earth ground and to the generator center/neutral as well.
However, I have heard that this will cause problems if unbalanced phases are used on the Step-Down, the neutral could wander from the zero position on the Generator side of the Step-Up transformer. This could cause an increase or decrease (cause instability) between the neutral and the different legs of the Y (generator side). As I will be using unbalanced loads on both sides of the transformer I want to try to avoid any instability.
It was recommended to me to leave the neutral/ground off of the Y side of the step up transformer, and instead connect the neutral/ground to phase #2 of the delta side of the transformer. Then connect the neutral/ground to the Y side of the step down transformer. I do NOT like the sound of this advice as it seems counter intuitive to have a grounded phase #2 on the delta side of the step down transformer and at the same time have the center/neutral of the Y side grounded as well.
Any advice or help that you could offer would be great!!
I am a newbie, so I will try not to make too much of a fool out of myself, but I need some help.
First of all, the problem: I don’t know how to properly ground a Generator -> Step Up Transformer -> Step Down Transformer.
We have a 27kva generator wired for three phase 216v Y with the center neutral earth grounded. This powers various motors and battery chargers at 216v and 125v, we are not using any three phase equipment at this time.
We also have a run of wires about ½ mile that powers another building, but we are getting too much line lose on this run. This is why I am trying to install the step up / step down Transformers.
The step up transformer is a 75kva 216v (depending on the taps) Y <-> 480v Delta transformer and the step down transformer is a 100kva 216v (depending on the taps) Y <-> 480v Delta. The step up transformer’s Y side is wired to the generator, and the Delta is wired to the Delta side of the step down transformer. I need to use the output of the step down transformer to power unbalanced 125v and 216v loads so I will need a neutral line.
I would think that the proper grounding would be to wire the center/neutral of both of the Y sides of the transformers to earth ground and to the generator center/neutral as well.
However, I have heard that this will cause problems if unbalanced phases are used on the Step-Down, the neutral could wander from the zero position on the Generator side of the Step-Up transformer. This could cause an increase or decrease (cause instability) between the neutral and the different legs of the Y (generator side). As I will be using unbalanced loads on both sides of the transformer I want to try to avoid any instability.
It was recommended to me to leave the neutral/ground off of the Y side of the step up transformer, and instead connect the neutral/ground to phase #2 of the delta side of the transformer. Then connect the neutral/ground to the Y side of the step down transformer. I do NOT like the sound of this advice as it seems counter intuitive to have a grounded phase #2 on the delta side of the step down transformer and at the same time have the center/neutral of the Y side grounded as well.
Any advice or help that you could offer would be great!!