rockman7892
Electrical
- Apr 7, 2008
- 1,178
I was having a conversation with someone today who wanted to install a set of CT's and associated ground fault relay on the secondary of a 3MVA 4.16kV - 480V Delta-WYE grounded transformer. The 480V secondary of the transformer is being connected to a 480V SWGR lineup through non-segmented Bus Duct and it has been requested that these CT's and relay be placed at the secondary of the transformer in order to pickup on ground faults occurring within the Bus Duct in order to prevent damage or explosion of the Bus Duct during faults. I have never seen this application on a 480V transformer of this size however it was stated that several Bus Ducts at this location have experienced faults and "blown up" or been significantly damaged.
On the primary of the transformer there is a 4.16kV fused switch directly connected to the transformer primary, and there is a 4.16kV feeder breaker upstream of the switch. The proposed idea would be to trip the upstream breaker when a ground fault was sensed on the secondary CT's through the dedicated ground fault relay.
As I stated I have never seen this sensing used for this size application so I was wondering if this was typical for this type of application? Is there a protection benefit to be gained by sensing this ground fault on the secondary and thus better protecting the Bus Duct? Is this worth the addition cost associated with CT's and relay? Any thoughts or past experiences would be appreciated. Thanks
On the primary of the transformer there is a 4.16kV fused switch directly connected to the transformer primary, and there is a 4.16kV feeder breaker upstream of the switch. The proposed idea would be to trip the upstream breaker when a ground fault was sensed on the secondary CT's through the dedicated ground fault relay.
As I stated I have never seen this sensing used for this size application so I was wondering if this was typical for this type of application? Is there a protection benefit to be gained by sensing this ground fault on the secondary and thus better protecting the Bus Duct? Is this worth the addition cost associated with CT's and relay? Any thoughts or past experiences would be appreciated. Thanks