Mbrooke,
the coordinates are 42°00'18.7"N 12°32'34.6"E.
In large substations the earthing resistance is low enough to avoid significant issues on touch and step voltages.
Generally, a 20 m x 20 m mesh is adopted. Equipment is generally grounded by connecting it to 2 different points of the ground grid, so that adopting a larger meshing would mean to increase the length of the grounding connections.
The earthing systems are designed according to CENELEC 50522 standard, which in turns is based on the current-time and voltage-resistance curves of IEC TS 60479-1. Considering the typical fault clearing time of 0.5 s and 1000 Ohm shoes resistance, it is quite uncommon to have problems inside large substations.
It is more usual to have some issues at the substation boundary, at the edges of the earth mesh or even outside the substation (induced voltages on third-parties).