JoeBaseplate
Structural
- May 31, 2011
- 204
Situation: New addition next to existing construction. There are no documents for the existing building so we have no idea what the existing footing capacity is like. Therefore I am reluctant to place any new loads on the existing. I am proposing the attached detail, basically using a cantilever grade beam to pick up the new column. The new addition is on story so the load not really that high (max 5 kips). Do the seasoned folks here see anything in this detail that I am missing or any other avenues I should be exploring besides the grade beam? The downside of this detail is that the interior wall footing has to be at frost depth too to pick up the grade beam but since they are talking winter construction, so that might not be an issue at all.
Thank you.
Thank you.