If the contractor did this and it was not the proper way in the first place, how sure are you the hole was the right diameter for the epoxy, the bolt is the right length, the correct type of epoxy was used (if this is a vertical face, then was a low viscosity/low sag epoxy used too prevent the epoxy from only coating one side of the bolt and hole), the hole was clean when they placed the epoxy, etc.... Also, these are in hollow core CMU's, another issue I have with it unless they were filled.
I have drilled and placed many types of anchors (horizontal and vertical) most of which required some sort of pull test to verify which you cannot perform with this type of installation. Anchor manufactures are very specific with the installations as they have already tested them.
Seems too risky to me, I would not sign off on it, unless you are absolutely sure of the installation and witnessed it. Especially if this is a overhead crane runway, not sure I would walk under it.