TMEldridge
Mechanical
- Sep 23, 2003
- 27
Client wants to install two gensets in one housing. This would mean we would have two belly (aboveground subbase) tanks side-by-side inside the housing. I cannot find any way to get around NFPA 30 requiring 3 ft separation (both tanks are greater than 660 gal and less than 3,000 gal). How can side-by-side belly tanks be installed, literally side-by-side, without violating NFPA 30?