You are a little off base there raghun.
Check a spec.
The standard generator in that size in North America will have six x 140+ Volt windings, two per phase..
For 120:208 Volts the phase windings are in parallel and the AVR is dialed down to 208 Volts phase to phase.
For 277:480 the phase windings are in series and the AVR is dialed up to 480 Volts, phase to phase.
For a do it yourself change over with mostly off the shelf parts:
225 kW = 281 KVA
281 KVA @ 208 Volts = 780 Amps
Each winding group will supply 390 amps.
Three 400 Amp breakers.
The breakers are mounted side by side and the existing 900 Amp . A sliding metal plate is mounted in front of the breaker covering the breaker handles.
Slots are cut in the plate for the breaker handles.
In the left most position the number 1 breaker is closed. The slots are such as to block the closing of the other two breakers when breaker number 1 is closed.
When breaker number one is opened, and the 900 Amp breaker is opened, the plate may be moved one position to the right. Now breaker number 1 is blocked open, the 900 Amp breaker is blocked open and breaker number 3 is still blocked open. Breaker number two may now be closed.
When breaker number two is closed, the plate may be moved to the last position on the right and breaker number 3 may be closed and the 900 Amp breaker may now be closed.
Connections.
Breaker #1 closed, 277:480 Volts.
Breaker number 1 connects T4-T7, T5-T8 and T6-T9.
Changing to 120:208 Volts
Breaker number 2 connects T4-T5-T6.
Breaker number 3 connects T1-T7, T2-T8 and T3-T9.
Adjust the AVR for the correct voltage before closing the 900 amp breaker.
The first few times, check the stability.
It's late and I'm tired. If I get a chance tomorrow I will draw a sketch of how the plate should look.
Bill
--------------------