Generator Vibration

Status
Not open for further replies.

cyw

Mechanical
Apr 3, 2001
3
I am going to acquire the vibratiob data of a turbine driven generator in few days time. The generator's vibration has been picking up since last month. I suspect it could be caused by soft foot/loosening support. Can anybody recommend what characteristic(s) that I should look for/what are the things that I should do during the data acquisition? I am going to use Bently Nevada proximity probes. Thanks.
 
Replies continue below

Recommended for you

Loose things can cause all sorts of harmonic nasties, but you'd expect to see a lot of third order (square waving) of your fundamental frequencies, as well as high frequency trash.

Well that was pretty techie...

Cheers

Greg Locock
 
Greetings the colleague!
In this case it is necessary to measure vibration in a vertical direction on basic paws of the generator and on the base. We shall tell 15 - 20 centimeters from a paw. The mode of operation of the generator should be nominal. In any case it is necessary to fix active and reactive power, and also a stator voltage.
For the Russian generator with nominal active capacity 200 MW the amplitude of vibration displasment should differ no more than on 10 microns (on how many I remember).

Dmitry Semenov
 