Rich246
Mechanical
- Oct 9, 2005
- 6
I'm looking for help with determining the cause of vibration in a generator. It is a 112mw air cooled unit attached to a gas turbine. This has been an ongoing problem for over a year. Initially we had high shaft vibration so balance moves were attempted. The shaft vibration was decreased after a number of moves but then we had casing vibration problems and axial vibration. Alignment was check and it was fine so they stiffened the generator by adding support plates from generator bearing to casing and added internal plates. This help some but over time the vibration has got worse. Recently if you change lube oil temperature or generator air temperature by a few degrees, the vibration would change. Now if you put any vars load on the generator vibration increases also. Exciter current has also increased by 50-75 amps higher than we normally see. Any ideas?