TraderJoe80
Marine/Ocean
- Feb 18, 2009
- 6
Another tug boat generator trip. Whenever we run our Port Generator and vessel is underway the generator trips. When sitting at anchor or along side the dock we have no trips.
Stbd generator is fine no matter what condition. Which leads us to assume some type of vibration is causing generator breaker to open.
This is what seems to be happening as observed by Chief Eng:
When load is placed from stbd to port gen say 80kw on port, it will immediately start to load to 90 then to 105kw and trip ( generator is a 150kw gen). Amps start at about 80 then gradually build to about 95-100 amps. Breaker finally trips at about 105kw and 155amps. I’m told the voltage stays at 480 the whole time, and the cycles are maintained at 60hz. Is this even possible? Do you think we could have a partial ground on the 480 line which is drawing some amps? The engineers aboard made no comment on the ground detection lights (which I’m waiting to hear back on). In E=IR if current is going up how come voltage isn’t dropping??? Is this possible?
I have an electrician going to visit the ship to take thermal imaging of the breaker and inspected contacts of main breaker. Do any of you have any other thoughts???
Stbd generator is fine no matter what condition. Which leads us to assume some type of vibration is causing generator breaker to open.
This is what seems to be happening as observed by Chief Eng:
When load is placed from stbd to port gen say 80kw on port, it will immediately start to load to 90 then to 105kw and trip ( generator is a 150kw gen). Amps start at about 80 then gradually build to about 95-100 amps. Breaker finally trips at about 105kw and 155amps. I’m told the voltage stays at 480 the whole time, and the cycles are maintained at 60hz. Is this even possible? Do you think we could have a partial ground on the 480 line which is drawing some amps? The engineers aboard made no comment on the ground detection lights (which I’m waiting to hear back on). In E=IR if current is going up how come voltage isn’t dropping??? Is this possible?
I have an electrician going to visit the ship to take thermal imaging of the breaker and inspected contacts of main breaker. Do any of you have any other thoughts???