Hi, I have three identical generators of 80 KW each.
At that size, forget three phase PTs an CTs.
The AVR will most likely be single phase sensing.
That makes reactive compensation easier.
The basic compensation is voltage sensing across phase A to phase B.
Compensating CT on phase C.
A quadrature ready AVR will have a two sense terminals and a compensation terminal.
There is a resistor between one sense terminal and the compensation terminal.
The sensed voltage flows through the resistor.
The CT is connected across the resistor.
Any real current from C phase will be at 90 degrees to the voltage sensed across A and B phases.
The voltage drop caused by the CT current will have negligible effect on the sense voltage.
However, reactive current will develop a voltage that is in phase with the sensed voltage and will either add or subtract from the voltage seen by the AVR.
If one CT is connected in reverse, you may expect issues when the power factor is other than unity.
A basic AVR may be used for reactive compensation with the addition of an external resistor and a CT.
It is common to have a switch that shorts out the CT when the unit is running alone.
Sets in that size range will have 3% droop.
Set your no-load frequency at 51.5 Hz or 61.8 Hz.
Freddy: I am under the impression that "cross current compensation" is another name for "quadrature compensation".
I may be wrong.
--------------------