Background:
During a scheduled unit SD, the generator rotor was taken out and the stator goes under rewedging and retaining rings replacement process. In the mean while the old protection panel was replaced with a new numerical one.
Incident:
When we synchronized a 153MVA generator to the grid, the generator tripped on split phase protection. The generator have a double winding each winding is 20 turns that is there will be 380V induced voltage for each turn for 13.8KV LL terminal voltage. If a single turn is shorted approximately 570A Circulating current will flow between the Paralleled windings. The split phase CTs are 3500:5 A and the setting is 40% inst.
What I am puzzled about is that, all three phases of the generator is showing a split phase differential current.
Is it normal or just something terrible gone wrong inside the generator?
After the incident the hire-ups come to the site and a lot of bla bla bla and at the end…the really mull operated or as they said too sensitive and they gave the clearance for machine rooling,
Once filed breaker is closed, I observed the differential current in the split phase input, it was below the pick up and for all phases. The chief decided to add a time delay of 60ms on the split phase element. At this moment there was abnormal humming sound from the generator, after the time delay the clearance have been given for synchronizing…..and then with a thundering noise the generator tripped but this time, the Buchholz relay of the main transformer operated on the second stage. Generator differential and overall differential element operated, when they open one end to inspect the generator, cracks have been found on the stator winding insulation.
My guess about what happened:
I think the problem exist before the first synchronizing attempt since the rotor was maintained by one contractor and the stator was done by another contractor.
The buchholze relay operation in the second time was because of the high inrush currents from the grid toward the generator, according to the relay records it reaches up to 60KA.
Any thoughts about what happened
Is it really possible to have split phase differential for all phases?
thanks
Background:
During a scheduled unit SD, the generator rotor was taken out and the stator goes under rewedging and retaining rings replacement process. In the mean while the old protection panel was replaced with a new numerical one.
Incident:
When we synchronized a 153MVA generator to the grid, the generator tripped on split phase protection. The generator have a double winding each winding is 20 turns that is there will be 380V induced voltage for each turn for 13.8KV LL terminal voltage. If a single turn is shorted approximately 570A Circulating current will flow between the Paralleled windings. The split phase CTs are 3500:5 A and the setting is 40% inst.
What I am puzzled about is that, all three phases of the generator is showing a split phase differential current.
Is it normal or just something terrible gone wrong inside the generator?
After the incident the hire-ups come to the site and a lot of bla bla bla and at the end…the really mull operated or as they said too sensitive and they gave the clearance for machine rooling,
Once filed breaker is closed, I observed the differential current in the split phase input, it was below the pick up and for all phases. The chief decided to add a time delay of 60ms on the split phase element. At this moment there was abnormal humming sound from the generator, after the time delay the clearance have been given for synchronizing…..and then with a thundering noise the generator tripped but this time, the Buchholz relay of the main transformer operated on the second stage. Generator differential and overall differential element operated, when they open one end to inspect the generator, cracks have been found on the stator winding insulation.
My guess about what happened:
I think the problem exist before the first synchronizing attempt since the rotor was maintained by one contractor and the stator was done by another contractor.
The buchholze relay operation in the second time was because of the high inrush currents from the grid toward the generator, according to the relay records it reaches up to 60KA.
Any thoughts about what happened
Is it really possible to have split phase differential for all phases?